New roof solar system (many questions)
So, back on track, the First guy's quote was about $42k, including a new roof. Seemed a bit expensive at the time, but many benefits would quickly make it very worthwhile. That is for 23 panels sized at 10kW production.
I got quotes from the second round, this time separate numbers for the new roof (with a few small additions) and solar. The numbers are quite shocking. The roof alone is over 20k, and the solar system
It is nearly 52k for an 11.7kW system. So the total project cost with the second option is over $72k before benefits. For now, I am still trying to wrap my head around such big numbers, and getting more clarity from both vendors to understand why so such a difference.
What is the rating of your electrical service at the panel? You can only produce 20% above the rating of your panel. If you exceed that it will not pass inspection by Federal law. That is NEC 24. I have a 200 amp service so, the most panels I can have is 20 which is 7.6 KW. That gets by as peak power never quite gets to spec. although mine will produce 7.5 KW in a bright noon day sun.
TankTop5
Update: I spoke with one solar company and their proposal, which includes a new roof. At this point, I was almost 100% decided not to go with the first guy as there were a few small but significant red flags, in particular, no breakdown of the new roof cost, and some weird energy estimation charts.
Speaking with the second solar company, which doesn't do new roofs itself but partners with an actual roofing company. The roofing guy stopped by yesterday to do a very detailed inspection of the roof and attic, and found and showed me a few small leaks already. We discussed a metal roof as well, but it doesn't seem like it would make sense to us to go that way. Guy is highly certified and seems like he really knows his only job - to do roofs.
His proposal will likely cost more than the first guy's, but I feel it's worth doing for many reasons.
Still pending to see the actual proposal from the second solar company, will update later.
I have been working in roofing for a couple years (1099 under a contractor and definitely don’t know it all) and any solar company that recommends a new roof before installing solar is ahead of 90% of solar companies. With few exceptions roofing isn’t too complicated but having a roofing and solar company that work together regularly is highly recommended.
BoredSysAdmin
BoredSysAdmin
I am not 100% sure, but my electrical breaker panel, main breaker, is "quad" looking with each of the smaller parts saying 200A, but there is one bar across them. similar to this breaker:
I assume it means my house also has 200A service. My outside electric company meter also says "CL200" among other markings on it.
Verdinut
Verdinut
A 200 amp house entrance has been very common in North America, since electric whole house heating started to be installed over 50 years ago.
So, that settles it, that you have a 200 amp service. So that means your best and most economical route is 20 solar panels with an output of 7.6 KW max.
Here are you other options.
1). Increase your electrical circuit current capability. That requires new panels at a minimum, and like I would have had to, you may well have to have your utility increase your electrical service power. In my case that would have required replacing the transformer that supplies the four houses on the circle.
My solar contractor was keen on increasing my electrical service with new panels. Actually that would not have been worth it. Luckily I ran it by Dakota Electric and found out that this was not a practical option.
2). Batteries for the excess power. This is not a good option and does not justify the expense in my view.
The reason becomes the i-squared power loss. Let me explain.
As you lower voltage current goes up by a reciprocal amount. However the power loss goes up by the square of the current. That is the physics of it.
Now to reduce those losses each panel has an inverter. Mine are 20% efficient which is the SOTA currently.
So the phase locked loop in the combiner synchronizes all the inverters with the AC mains from the power company. The panels output at 240 volts peak to peak +/-, like the US house supply. To keep the load even. Every other breaker is wired to the opposite phase at the panel to keep the load reasonable even between the 120 volt phases. 240 volt appliances are full phase at 240 volts.
So in order to use a cable down from the roof that is not like car battery cable the inverters output 240 volts AC.
Now if you have batteries then in addition to the 20% loss on the roof, you have another 20% loss converting it back to DC to charge the batteries, and then another 20% loss when you convert the DC from the batteries back to 240 volts AC. So you have three 20% losses instead of one. A very bad plan in my view. Now people try and sell this, but it is a bad idea. Round here code requires the batteries be in a structure not connected to the house, which in my view is sensible. So that makes 2 way metering by far the best option.
Now, the solar people will try and cover your roof with all the panels they can get on it.
However, I spoke with the chief electrical inspector for MN and the local inspector for Eagan/Mendota Heights. The latter was a really nice guy and very experienced and reviewed the whole situation with me. That saved me huge mistakes.
These solar companies will not explain the NEC rules. Mine did and included new panels, but that made the cost prohibitive and Dakota Electric explained that solution was wide of the mark.
So then I got a plan submitted that met all Federal NEC codes and local codes.
Now, my company was pretty cooperative once they realized I know the regs backwards and forwards. They actually I think, got a little scared of me. From then on out I only dealt with their most senior engineers and we got into a really good working relationship right away.
So plans were sent to an fro and we came up with the optimal plan. Note avoid dealing with marketer and MBA types. As you know I have visceral loathing of those types and can spot them a mile off.
My case was complicated by the fact with an ICF home the combiner, fireman's switch and reverse meter can not be mounted on the house.
So I had to design that free standing structure and have a concrete foundation laid for it, with it mounted to code. I designed it, and built it with my son in law in three hours. I previously mounted the L-anchors while the concrete contractor was here, and the concrete still liquid and wet. I had to be really precise in my measurements as there was no redo. I had to pay attention to the equipment spacing according to NEC and issues like that. How the above three devices are mounted is in the codes.
Anyhow it is a very strong design and won't go anywhere.
All the planning paid off, and it passed electrical, Dakota Electric inspections and building inspections first time with zero issues or queries. From what I have been told this is highly unusual round here.
So, it has been up and running for 8 months now with no issues, and produced 8.6 mega watts to date.
So I think we are on track to meet the design criterion to replace 65 to 70% of our annual electricity consumption.
The cost was $42,000 before the tax rebate. So, this is going to cash flow, and will for you if you get it up and running by the end of the year.
This installation is now in the Enphase engineers teaching file, in particular in how to install solar on an ICF home, which they had not done before.
I am really pleased with the Enphase equipment and their software support for system monitoring.
Be careful, the inspectors warned me that there are sharks and bad practice out there all over the place.
The local inspector told me that it was highly unusual to pass a solar installation first time round here.
If you have further questions ask. Now is the time to get you system right, and don't expect to get the correct information from the vendor first time. I did not, and I advise you to make sure they know you ARE IN CHARGE. Like i did, you might have to let them know that right up front. You can only do that if you know what you are doing.
I strongly recommend you run your design by your local electrical inspector before signing the final design. Horror stories abound in this area, according to the inspectors I spoke to.
So don't let your contractor do something you feel is not right. If you are not sure talk to your local electrical inspector. Don't be afraid to be a PITA, one of my specialties. I shut the project down twice as I knew practices were not optimal. Third time they followed my master plan. So make sure your project is right by design.
If you want standby power then and free standing auto start generator is by far your best option, over and above your solar installation. I have to have that for medical reasons.
BoredSysAdmin
BoredSysAdmin
@TLS Guy
I asked about system sizing and production and here's my question and vendor reply:
Me:
I believe my house has a 200A electrical service. Someone online mentioned I
could only go up to 7.6KW solar before it fails the NEC 24 code?
Vendor:
This all has to do with the net metered back feed into the grid. 7.6KW
would require a max over current protection of 40amps, which is the
largest size breaker we are allowed to back feed into your main 200amp
panel. However, we can back feed at other locations without that
restriction; and it is standard best practice to do so.
o Such a statement is likely to be due to a low skilled installation team not
being more familiar with such standard practices. Any licensed electrician
would know this. However, most solar installation companies do not use
licensed electricians during installation, often only using one for stamping
one-lines or if needed, to respond to an inspection failure.
o We have a few clients with 200A service & 200a MDPs with systems
larger than 75KW. It’s all how we manage the back feed.
@TLS Guy
Me:
Vendor:
Our electrician was licensed. Dakota electric would not allow us to backfeed above NEC. We do back feed as much as we are allowed, but the local infrastructure and our electric utility will not allow us to exceed NEC. I argued with them about that to the bitter end.
BoredSysAdmin
BoredSysAdmin
I don't think anyone is suggesting backfeeding more than 7.6kw to the grid. The current vendor says to limit backfeeding to the utility and redirect the rest to house consumption. Not sure how it's accomplished.
I will not argue that point more than this, simply as I don't understand it sufficiently, nor do I have much desire to learn it in such minute detail. I expect a licensed electrician to install such a system, which will pass my township electrical inspection, ideally on the first attempt.
That sounds like absolute nonsense unless your supply to the house can safely take over 220 amps. I suppose in some circumstances it might, but I bet most utilities are like Dakota Electric and don't put in bigger cables and transformers than the design spec. requires. That is not an unreasonable point of view.
The real problem with this is that I don't have enough load in the house to get even close to 200 amps. But say I did, then in full sun the system would have to take 220 amps and that is the wiggle room of NEC 24.
So this issue is that if I sold the house the new owners might load it to 220 amps. I highly doubt it, but I can't say it would not happen.
So, I floated the idea of an inductive current sensor on the cable going into the entry panel that would shut down the panels if the current exceeded 200 amps or even 180 amps.
The state of Minnesota was up for it, but Dakota Electric wanted double redundancy. So then I gave up.
I have just got my bill for what is historically our peak usage month. We used 1628 KWH and the solar production was 1328 KWH which is 82% of our usage. Our consumption for this period has been very consistent. So this is a bit better than my projections for this period where I estimated 65 to 70% solar production.
I should be a bit clearer about what that vendor told you about feeding the power back into you house to get round the NEC.
I got told the same nonsense. Here is the math. You have a 200 amp panel. So if you did consume 200 amps and the panels produced more then the NEC of 7.5 KW, your main breaker would trip for a start and you would be no further ahead. So in order to do what they are trying to sell you, you would have to replace your entry panel at least and probably the feeds to you interior panel/panels. I can tell you it is absolutely not worth it.
The first proposal I received was just like the "canard" that has been proposed to you. It struck me, that it was nonsense scheme and the inspector agreed, that he would not pass it without extensive changes to the homes electrical system, and that would be in no way worth it.
So be really wary of these designs these solar vendors come up with. What you don't want is an installation installed that can not pass final inspection and can't be activated.
So my advice is if you have a 200 amp service, which I believe you do, then stick to NEC 24 and just install 20 solar panels. From me first 8 months that looks like the correct cost effective solution if your house has a 200 amp panel.
eljr
eljr
I guess in your neck of the woods, where calendars show the 18th century and horse carriages roam the unpaved streets, occasional masked bandits gallop through the main street. I assume in such an "idyllic community filled with charming homes", solar panels would definitely stand out. In fact, they would serve no purpose at all, just like your comments on this thread so far.
That said, in my neighborhood, one of the most affluent in town, solar panels are nearly on every 5th roof.
Calendars show 19th century, no horses, streets are cobblestone. This my new home.
Home I am leaving is circa 1920.
My first home was built in 1900 and sported an elevator in the foyer with a sitting room off the master. Back bedroom had a sleeping porch for summer nights.
Top floor were the servant quarters.
Yeah, not as many people prefer old if they can have shinny being
BoredSysAdmin
BoredSysAdmin
Few updates: So far I got three quotes for solar.
One is for 42k and includes a new roof. The estimated cost for solar alone is about $28-30k for 10kW system.
The Second one is for the roof and solar from two separate (but connected) vendors. For 21k roof and 51k solar for 11.7k system.
Last one is for solar only and it's for 10.7kw system and costs 33k
Clearly second vendor is 20k more expensive, even for a slightly larger overall system is way off the mark on pricing, but the second roof vendor,r I think I can trust more.
One thing that I see fairly common is that both the 1st and 3rd solar companies seem to vastly overestimate solar production based on ideal case scenarios.
About NEC codes and backfeeding, the explanation I got is that they plan to tie in between the meter and breaker panel; this way, the over 40-amp backfeed will not overfeed the panel and flip the breaker. I am not an electrician, but a licensed electrician told me this is a widely accepted practice, and it will pass the city electrical code inspection. Again, I am not an electrician and will not argue with you or the solar company about whether it's best practice or not.
You need to be very careful here especially if you don't follow NEC.
My company wanted to fill the roof with panels and gave me the same story, that you could backfeed the excess back to the utility. Usually you can't. The inspector warned me about this and said he would not pass it, because the utility would not hook me up.
So when I spoke with Dakota Electric they said I absolutely had to follow NEC or they would not turn on the reverse meter, or actually install it.
So then I got the correct design.
Now the utilities position is not at all unreasonable. To keep costs down they really don't want to over build. This was a new development seven years ago. It was agreed that there would be four houses with 200 amp service. This is usual and entirely reasonable. Now that transformer in my pictures is sized for such, plus a little wiggle room. So if I exceeded the NEC then I would exceed my tap on that transformer where it has four secondary taps each rated for a 200 amp service. So, at the very least I would have had to replace an expensive transformer.
Now there is an even bigger issue, as if solar systems proliferated that exceed the NEC then the utilities would have a load management nightmare.
Electricity once generated has to be used right away. Generally utilities do not have large battery facilities, which in any case are wasteful because of all the conversions. Moment to moment load management is a big task and responsibility of electric utilities. So if you have a bunch of solar panels in an area, then local loads would likely become unmanageable depending on instantaneous variation from cloud/sun, leading to transformer station breakers tripping. So, I have everry reason to believe this was all part of the NEC code. In other words there is chaos avoidance behind this reg.
Funnily enough we have a big court case pending in Minnesota over this.
There is a large Indian reservation casino, that has just installed a very large solar system at their facility. They want to sell excess back to the utility, but the utility has refused to hook up their solar system, on the grounds that it beyond the limit of their current infrastructure to safely control the power provided. They say, that the investment would require a rate increase across the network.
Of course this is all in the local papers. As you might expect, pig ignorant Joe public is totally unable to grasp the technical challenges and issues involved here.
A pig part of the problem is that power station can not lower their power production on a moment to moment basis. This is especially true of nuclear energy, of which we have a significant amount in this area. Funnily enough, this is one advantage of wind generation as they can quickly be turned away from the wind. So you get letters to papers decrying the fact that on a windy day a lot of these wind farms have units not turning. Well the reason is that there is nowhere for the power to go at that particular moment without causing catastrophic damage to the distribution infrastructure.
My final comment is that teaching of the core sciences like physics and chemistry is rock bottom abysmal right across the board in the US. So I had to teach my kids, and three entered technical fields and have excelled. Change is long overdue. Less woke BS and more that helps kids earn a decent living and truly deliver what Trump wants, but that his tariffs won't. The Asians are not making this mistake.
eljr
eljr
First, thanks for making this political and for the record it is the deploables who do not excel academically.
Clue, Trump wants to bullshit you and line his own pockets. Nothing more.
What we need to teach the kids starting in kindergarten is critical thinking. This is the real tragedy. Americans can't think objectively. If they could, we would not be in this mess now
They also have to be given the right facts and didactic instruction in order to have intelligent thought. You do seem to come across as a petulant rabble rousing nut job lately.
dlaloum
Quick observation - Spring is finally here in Melbourne, Australia, my 6.6kw solar PV system, totally charged my 10kwh battery yesterday... keeping our home powered by the sun from around 9am to around midnight...
Battery was fully charged by 2:30pm, and between 4pm I fed 1.2kwh back to the utility (for basically peanuts... they provide the government mandated 5c/kwh for feed in.., while charging 30c to 40c / kwh)
Having many of my panels oriented east/west means that I stop drawing power from the grid earlier in the morning, and return to battery and/or grid power later in the afternoon.
Total power generated is lower... however my panels are sufficient to charge my battery when the sun is out (about 9 months of the year) and keep me from using grid power during the day.
With our power use, I could use more PV panels, if I had a larger battery (currently considering a storage upgrade to my battery bank) - but a larger battery won't provide me much benefit, without more panels....
I know our Australian system differs from the USA and other nations - but some of the generic considerations are the same - so here is another reference point for those interested.
dlaloum
As an aside - we received notice that there was "likely" to be power outages tomorrow due to maintenance on the power lines (from previous experience, likely = definitely) - from 9am to 4:30pm.
I went into my battery setup, and changed to UPS reserve from 15% to 90%... tomorrow, I can see out the day with utility power out, without any major concern.
My internet provider also warned my that by hybrid coax link service may suffer an outage tomorro, presumably due to loss of power in the area - not a major concern as I have 5G mobile backup on my router.... and the router sits on my battery backed circuit, along with a few critical services such as the fridge, microwave, and the "stereo"/TV (not that it's been "stereo" in decades!)
I work from home (frequently) - and the only thing I may miss, is the AC/Heating.... but given it's spring, I am unlikely to need it. The AC/Heating is NOT on the battery circuit - if I lived in an area with serious winters, I might have designed it differently. As it is, the loss of heating is not a big concern given our climate, although during a heatwave, the loss of AC could make for some discomfort... still we are a coastal city, so we typically don't get many really nasty heatwaves.
trochetier
A friend who lives in DE has a net metered huge solar system I think 18kW his house has a 200 amp panel. The house all electric, it has two heat pumps, (keeps his house about 78F during the winter), and has a hot tub that's a electricity guzzler.
That would be tough to do that on a 200 amp panel. But the other issue is what is the rating of his service to the house from the electric company?
That would potentially add another 75 amps to 200 amp service. So if he exceeded 200 amps, the main breaker would trip. You would not get away with that in this jurisdiction and frankly nor should you. To make that properly safe would require 450 amp service at least. So, I doubt that installation conforms to NEC.
carlosmiguez75
The whole 200A service debate usually boils down to how much you trust your installer's license versus their sales pitch. A lot of guys will tell you that 7.6kW is the hard ceiling for a 200A panel because of the 120% rule, but that’s only if they’re taking the easy way out with a standard breaker backfeed. Line-side taps are the standard for a reason, even if some inspectors are cranky about them.