My wife called the other day and said we are having A/C problems again. We've had problems ever since we bought the house. It would work for awhile then it would flip the circut breaker. We've had two different techs look at it and said everything was find. The last tech tighten the wires connected to the break saying they were a bit loose but here lately it is causing the breaker to flip again.
I think we just need an additional unit as we supposably have the biggest residental a/c unit sold but our 2200sq/ft house is just too much for it when it gets really hot.
Matt, also have him check it with an Amp Probe. It may be drawing too much while running, due to the compressor going bad.
If the label calls for fuses, there MUST be a fuse, as the disconnecting means, not a circuit breaker. If the label calls for a "HACR" type breaker (Heating, Air Conditioning and Refrigeration), then that is the type of breaker that must be used. Both as TLS mentioned will be a 'slow blow' type.
The NEC rules for protection of motor circuits are different than for circuits with simple resistive loads. When a motor first starts , it draws a higher amount of current than it does after it is running. The high "inrush" current can exceed the rating of a breaker or fuse sized to protect the wire. The inrush current lasts a second - less time than it would take to damage the wire or its insulation. However, if the overcurrent device is sized to protect the wire against overloads, the device might trip, and the motor would not be able to start.
Motor circuits get around this problem by dividing the two separate functions of an overcurrent device. "Overloads" are currents that can damage a circuit if allowed to continue for a sufficient time, whereas "short circuits" and "ground faults" are high currents that can cause immediate damage. Large motors and air conditioners separate these overcurrent functions. The breaker or fuse ahead of the air conditioner only protects against short circuits and ground faults. Overload protection is built into the compressor itself. The wire to a condensing unit must be large enough to allow the equipment to start. The device is therefore not sized to protect the wire against overloads.
Good Luck,
Rick