Okay so you think this Belkin device is sufficient. I will use that then. Thank you.
What I meant was a UPS is fine not that particular unit. For one thing I suspect it is too small to drive a receiver. Published specs are pretty nonexistent for that Belkin unit and its too cheap to be any good for powering an AV system.
What you need is a UPS that will provide to VA rating of the device and the continuous power on watts. AC devices have true power and apparent power. The VA rating will tell what power is available to meet the apparent power needs and the true power is the actual power consumed over time.
This all comes about because current and voltage have a phase angle, which varies with the device. In other words current and voltage are out of phase. As a rule if thumb the continuous power rating is usually about 30% less than the VA rating. So your unit probably provides 700 to 900 watts continuous.
The other thing is how quickly the UPS responds. An acceptable response for transfer to battery is 1 to 5 msec for a significant line fluctuation.
APC are the real leaders in all this and you want to look at what they have to offer.
There should be no noise problem, my UPS units are in the three racks as you can see. There should be no difficulty with your cable management plan.