Oh, here's a paper written by Martzloff that describes how a "whole-house" protector can't protect from every aspect of a lightning strike.
Martzloff's paper (section 2) demonstrates what happens when the single point earth ground is not properly implemented. Figure 1 - wires enter or leave buildings without the always required service entrance earthing. We once saw same. Computers networked to two buildings. The ethernet cable was not earthed where it entered each building. Therefore a strike to building one was a direct strike to computers in building two. Building one acted as a lightning rod connected to computers in building two - because wiring was also defective as in Martzloff's Figure 1.
In Martzloff's example, surge energy was permitted inside the house - via the sewer pipe vent. Because that energy was permitted inside the building, then it found paths to earth via appliances - ie the kettle. Martzloff says a high current 'whole house' protector is insufficient. Of course. A protector is only as effective as THE most critical component in any protection system - earth ground.
Martzloff demonstrates that we cannot test our protection systems. Therefore if damage results, an owner must locate and correct a failed or defective earthing path. In his case, lightning found earth ground destructively via aluminum foil insulation resulting in fire. So he corrected that mistake. Martzloff discusses damage between buildings because single point earthing was not installed. Even a ‘whole house’ protector is insufficient without proper earthing. Of course. A protector is only as effective as its earth ground. Why is this wrong only because jneutron insults with acidic words?
From IEEE Standard 141 (Red Book) says:
> In actual practice, lightning protection is achieve by the process of interception of lightning produced
> surges, diverting them to ground, and by altering their associated wave shapes.
I am confused why you are asking for information that is this standard from numerous professional sources. jneutron only read enough to post caustic remarks based in Limbaugh spin. He is the kind of ‘engineer’ who gets people killed. His ‘knowledge’ can only have credibility when one is mystified by his spin. His wacko attacks are no relevant.
What do you want to know? If the well proven concept of earthing surges is difficult, then what specifically confuses you? Routine is to have direct lightning strikes without damage. This is done routinely in facilities that never waste money on plug-in protectors. That routinely and carefully earth ‘whole house’ protectors. Because a protector is only as effective as its earth ground. Why (or what) is that confusing?
Is this what you want? From AT&T’s "Grounding and Bonding for Network Facilities”
> 5.3.5.3 Inductive Reactance
> The impact of inductive reactance at high frequencies can be demonstrated by comparing the DC
> resistance and inductive reactance for a #6 AWG wire. The DC resistance for 10 feet of #6AWG wire is
> 0.00427 ohms (column 3 times 10) while the inductive reactance for the same wire at 1Mhz is 24 ohm
> (column 6a) - over 5000 times as large. This is why there is so much emphasis on reducing
> inductance in our grounding infrastructure by using the shortest possible wire routes and
> minimizing all bends.
George Kauffman discusses in "Get grounded: Protecting Electrical Devices from Lightning Transients" in Electrical Engineering Times:
> Providing a flow path for the lightning current is central to effective lightning protection. ...
> Another aspect of impedance ... of a wire is predominately related to its length and weakly
> related to its diameter. ... The length of the cable increases the impedance dramatically.