I use standard computer APC UPS units of the correct power. Remember VA is not watts for an AC circuit, only a DC circuit. Do not connect power amps to UPS units.
For the phase angle of a home AC circuit 300 watts is 500 VA. So your UPS will be specked in VA, but your processor will be specked in watts. I would get a unit over specked by 25%. So if your unit draws 1200 watts for instance then you should get a 2,500 VA UPS.
One other thing, get whole house surge protection installed at entry to your residence. If you can't do it at entry, then do it at the panel. Do not use surge protector strips. Doing at entry gives you the best protection and protects everything in your house. This is now code in many places now, and should be everywhere. That is actually the most important item to protect your gear. Whole house protection saved me a boat load of trouble last summer with a direct hit.