You could do one of two things.
Run EMT,(thin wall metal conduit) it's a little more expensive; though it will pass any inspection, if properly terminated.
The other choice, is to ask both, the building and electrical inspectors, if PVC would ok.
It will also need a connector and plastic bushing, to be considered properly terminated.
All conduit should be big enough to pass cable jacks, etc.
With the NEC, the local authority has jurisdiction. They can require something above and beyond the code.