To keep you updated. Beltrami Electric replaced the transformer to one of greater capacity today. I post the results today in a communication with the power company. I find this all very interesting. It helps to have clue.
Dear Sam,
I was just about to Email you. The transformer in the yard has just been changed for one of increased capacity. I have now done careful measurements and taken a picture. The news is largely good but not perfect.
The RMS voltage now measures 120 volts in the studio. The peak to peak Voltage measured on my Tenmar scope, is 170 volts. The wave form is improved. It is no longer clipped and it is symmetrical. Calculating the RMS from peak 170 volts X 7.07 gives a calculated RMS voltage of 120.19 volts. This now agrees with the RMS meter indicating you now have a wave sinusoidal in nature. The RMS readings of your previous wave were of limited value and inaccurate.
The distortion products I measured very carefully with my HP distortion analyzer and it is exactly 9% THD. It was 34% The IEEE recommended maximum for a power system is 5%.
I will post the pictures. The high frequency distortion products do not show on the picture of the wave, however they are visible on the scope. I would say fluorescent lights and SCR dimmers through out your system are the most likely cause of what I'm seeing.
Here is the wave from the old transformer.
http://mdcarter.smugmug.com/gallery/4320551_3HKkR#253385889
Here is the wave from the new transformer.
http://mdcarter.smugmug.com/gallery/4320551_3HKkR#254135322
Even these pictures show the considerable improvement.
Please could you make sure you send this communication to your engineer. Please send me his Email address and I will communicate with him directly. It is a good teaching case. Also I think it would be in the interests of Beltrami electric to filter out this THD and get it to 5% or less.
I do appreciate the response of Beltrami electric to my problem. I still want this formally registered as a compliant, so it gets on your radar. I also want the compliant marked as incompletely resolved at this time. However I think my equipment will be much less stressed by what has been achieved. Above all I appreciate an MD practicing electrical engineering without a license being taken seriously.
I'm pretty sure this problem has taken out the lower level HD DVR. A Direct TV technician is coming to check the wiring tomorrow, but I know it's OK. I'm sure that lower level unit will have to be replaced for the second time, but I'm hopeful that with what you have done, and what I have done, that will be the last of it.
Once again, thanks for your efforts.
Best Regards, Mark.