Thread: Panamax-Furman MIW-XT Remote Power Review

  1. #1
    admin is offline Administrator admin should be listened to
    Join Date
    Apr 2004
    Posts
    96
    Thanks Given
    0
    Thanks Received
    1,226

    Arrow Panamax-Furman MIW-XT Remote Power Review

    If you want a flat panel to "float" on a wall, you're going to need to run power to it without risking burning down the house. The MIW-XT is an all-in-one solution that might just fit your needs. With a dedicated power run and a space for a Decora-style insert, adaptor for keystone inserts, or a rubber grommet passthrough, the MIW-XT can accommodate your power and cabling needs.


    Discuss "Panamax-Furman MIW-XT Remote Power Review" here. Read the article.

  2. #2
    Bryce_H's Avatar
    Bryce_H is offline Senior Audioholic Bryce_H is gaining some recognition
    Join Date
    Oct 2004
    Location
    Colorado Springs, CO
    Posts
    543
    Thanks Given
    0
    Thanks Received
    19

    Default

    I have an older version of one of these for my project (on the ceiling) and installed it when I finished the basement into a dedicated HT. Everything worked great and it allowed me to have my projector plugged into my surge protector in the component closet. Agree a touch on the pricey side, but better than needing to replace a blown projector
    I reject your reality and substitute my own - Adam Savage

  3. The Following User Says Thank You to Bryce_H For This Useful Post:

    Clint DeBoer (09-23-2009)

  4. #3
    Omega Supreme's Avatar
    Omega Supreme is offline Audioholic Omega Supreme has a small fan club
    Join Date
    May 2005
    Location
    Alabama
    Posts
    162
    Thanks Given
    32
    Thanks Received
    19

    Default

    A couple of questions. Is it really dangerous to run a good quality 12ga. extension cord in and interior wall? I have a 12ga. ext. cord that I use for a air compressor, saws, shop lights (and other shop tools) that never even gets warm. I also have a cheap 14ga (I think) ext. cord that I use for my lawn edger and leaf blower that doesn't get hot or even warm. Wouldn't these pull more current than a TV.? My 50" plasma came with a cord that was about 6' long and I have it running thru the wall (about 4' is in the wall). It has been that way for about 5 years. Should I redo it so it isn't running in the wall? I didn't realize the TV’s power cord was not rated to run in-wall. Anyway, if I need to redo this could I just not make an extension cord out of some 12ga romex that I have laying around. That would probably cost about $4 instead of $150.
    The Omega Supreme System
    Denon 3805, Def. Tech. BP7002, CLR 2500, BPX, Panasonic TH-PX50U

  5. #4
    Rickster71's Avatar
    Rickster71 is offline Audioholic Spartan Rickster71 should be listened to
    Join Date
    Jan 2006
    Location
    N.J.
    Posts
    5,516
    Thanks Given
    3,478
    Thanks Received
    3,212

    Default

    Quote Originally Posted by Omega Supreme View Post
    A couple of questions. Is it really dangerous to run a good quality 12ga. extension cord in and interior wall? I have a 12ga. ext. cord that I use for a air compressor, saws, shop lights (and other shop tools) that never even gets warm. I also have a cheap 14ga (I think) ext. cord that I use for my lawn edger and leaf blower that doesn't get hot or even warm. Wouldn't these pull more current than a TV.? My 50" plasma came with a cord that was about 6' long and I have it running thru the wall (about 4' is in the wall). It has been that way for about 5 years. Should I redo it so it isn't running in the wall? I didn't realize the TV’s power cord was not rated to run in-wall. Anyway, if I need to redo this could I just not make an extension cord out of some 12ga romex that I have laying around. That would probably cost about $4 instead of $150.
    It's not the size of the wire that's the problem; it's the insulation.
    The insulation on the cord is not approved for in-wall use, it against the electrical code.
    Romex is the way to go for in-wall.

    What it comes down to is; insurance companies are looking for any excuse to not pay a claim.
    'If' you ever have an electrical fire, and the insurance adjuster saw the extension cord in the wall. (code violation)
    They wouldn't pay the claim.

  6. #5
    Omega Supreme's Avatar
    Omega Supreme is offline Audioholic Omega Supreme has a small fan club
    Join Date
    May 2005
    Location
    Alabama
    Posts
    162
    Thanks Given
    32
    Thanks Received
    19

    Default

    I guess I understand why an extension cord is not rated for in-wall use because you could have various appliances plugged into it. The extension cord mfg. can't calculate what load people will put on it to say it is safe for in-wall use. I guess that is why that extension cords are against code. But the TV mfg. knows what load the TV will use thus able to create a power cable that will be safe in your wall. Is the TV power cable not rated for in-wall use? I looked at my manual online and it did not have any info. that said that you could not run it in-wall. I know that the wire size is not the issue (unless you’re trying to run a heavy load on an old 18ga. Cord) but the insulation is. But the insulation on the power cord from my TV is 5 times that of romex.
    The Omega Supreme System
    Denon 3805, Def. Tech. BP7002, CLR 2500, BPX, Panasonic TH-PX50U

  7. #6
    Clint DeBoer's Avatar
    Clint DeBoer is offline Administrator Clint DeBoer should be listened to
    Join Date
    Jul 2002
    Location
    Lakeland, Florida, United States
    Posts
    6,153
    Thanks Given
    509
    Thanks Received
    805

    Default

    Quote Originally Posted by Omega Supreme View Post
    Is the TV power cable not rated for in-wall use?
    Nope. Gotta use 12/2 power cable in-wall. It's not going to be code no matter how much you want to break the rules... lol.
    Clint DeBoer
    Editor in Chief
    Audioholics

  8. #7
    Omega Supreme's Avatar
    Omega Supreme is offline Audioholic Omega Supreme has a small fan club
    Join Date
    May 2005
    Location
    Alabama
    Posts
    162
    Thanks Given
    32
    Thanks Received
    19

    Default

    I’m not trying to be hard headed here but what does the code say? Is it really unsafe to run the TV power cord, that is only handling the load of the TV and has a lot more insulation than 12/2 power cable, in the wall? It just doesn't make sense to me.
    The Omega Supreme System
    Denon 3805, Def. Tech. BP7002, CLR 2500, BPX, Panasonic TH-PX50U

  9. #8
    Rickster71's Avatar
    Rickster71 is offline Audioholic Spartan Rickster71 should be listened to
    Join Date
    Jan 2006
    Location
    N.J.
    Posts
    5,516
    Thanks Given
    3,478
    Thanks Received
    3,212

    Default

    Quote Originally Posted by Omega Supreme View Post
    I guess I understand why an extension cord is not rated for in-wall use because you could have various appliances plugged into it. The extension cord mfg. can't calculate what load people will put on it to say it is safe for in-wall use. I guess that is why that extension cords are against code. But the TV mfg. knows what load the TV will use thus able to create a power cable that will be safe in your wall. Is the TV power cable not rated for in-wall use? I looked at my manual online and it did not have any info. that said that you could not run it in-wall. I know that the wire size is not the issue (unless you’re trying to run a heavy load on an old 18ga. Cord) but the insulation is. But the insulation on the power cord from my TV is 5 times that of romex.
    It has nothing to do with the ampacity of the wire. A receptacle can be overloaded just as easily as a power cord.
    It has to do with flame spread. Romex and / or in-wall rated wire won't support combustion, once the ignition source is removed.
    Power cords are considered temporary by the NEC (National Electrical Code) and are not rated for in-wall use.

    An extension cord does not have more insulation than Romex wire. It's also the 'type' of insulation that counts.
    Last edited by Rickster71; 09-23-2009 at 08:07 PM.

  10. #9
    highfigh's Avatar
    highfigh is offline Audioholic Spartan highfigh should be listened to
    Join Date
    Sep 2008
    Location
    Milwaukee area
    Posts
    6,263
    Thanks Given
    16
    Thanks Received
    1,583

    Default

    Quote Originally Posted by Omega Supreme View Post
    A couple of questions. Is it really dangerous to run a good quality 12ga. extension cord in and interior wall? I have a 12ga. ext. cord that I use for a air compressor, saws, shop lights (and other shop tools) that never even gets warm. I also have a cheap 14ga (I think) ext. cord that I use for my lawn edger and leaf blower that doesn't get hot or even warm. Wouldn't these pull more current than a TV.? My 50" plasma came with a cord that was about 6' long and I have it running thru the wall (about 4' is in the wall). It has been that way for about 5 years. Should I redo it so it isn't running in the wall? I didn't realize the TV’s power cord was not rated to run in-wall. Anyway, if I need to redo this could I just not make an extension cord out of some 12ga romex that I have laying around. That would probably cost about $4 instead of $150.
    It's not only dangerous but it doesn't meet any electrical code. Use Romex and you'll be fine, even if it's installed where an electrician is required for live circuits, as long as one end requires an extension cord to connect it to some power source. Without the extension cord, the circuit is dead.

    The extension cord can't be used inside of walls, over a concealed ceiling or below ground.

    This also has some filtering (no, I don't want the flame throwing BS to start again).
    Never eat anything that squirts out of a machine.

  11. #10
    highfigh's Avatar
    highfigh is offline Audioholic Spartan highfigh should be listened to
    Join Date
    Sep 2008
    Location
    Milwaukee area
    Posts
    6,263
    Thanks Given
    16
    Thanks Received
    1,583

    Default

    Quote Originally Posted by Clint DeBoer View Post
    Nope. Gotta use 12/2 power cable in-wall. It's not going to be code no matter how much you want to break the rules... lol.
    14/2 would be fine if it's a 15A circuit.
    Never eat anything that squirts out of a machine.