My pre-pro (Marantz AV7005) consumes 60W of power.
I bought a Tacoma 100VA step-down transformer for it after I bought the unit when I was told that 90VA and above would suffice.
So, if the step-down is too weak, how do you calculate the required amount of power for the step-down?
Also, I would expect the pre-pro to not even power on if it receives too little power. Am I wrong?
Thanks again.
Unfortunately you are wrong. You are dealing with an inductive load, and what is worse the load will not be constant, depending on the power drawn by the processor.
The VA rating you require is 60 watts divided by the power factor. This will be less than one. I do not know the power factor for that unit, so I can't calculate what you require.
The problem comes with the fact that voltage and current are not in phase with inductive loads. So you have the issue of true and apparent power. Now whist the true power will be 60 watts, the apparent power can be much higher. The supplying device must be able to meet the current demands of the apparent power needs. In practice this means that momentary current draws can be much higher than imagined. So when demands are not met then the AC waveform becomes clipped. This can lead the unit to malfunction and can do permanent damage. It will not stop the unit powering on.
The power divided by voltage to get the current draw only applies to a resistive load in an AC circuit. So we do not know the current draw from your unit even if plugged into an outlet of the correct voltage, but it will be higher than 60/110.
This is how people so often end up on the rocks with step down transformers. You are not the first by a long shot.
From the fact that this unit worked from a 200 VA transformer and not your 100 VA one, leads me to believe that your unit does not meet the current demand required to meet the apparent power requirements of your pre/pro.
So my rule of thumb is to advise a step down transformer have a VA rating in the range of 1.5 to 2 times the rated power in watts of the device.
To be honest I never advise units to be used in jurisdictions they were not designed for. It leads to many issues. I advise selling before leaving the country and replacing it in the destination country.