The telephone pole, that is..
I was walking around town with my sweetheart a couple of nights ago, when I spotted a problem with the AC feed to a building..(yes, I'm a geek...I can't help it..)
On Long Island, the power feed to buildings is this:
1. High voltage three phase wires at the top of the poles..the neutral wire for that set is lower on the pole.
2. Whenever required, a one bushing transformer is put on the pole...one of the 3 phases is connected to with a jumper, and it goes down to the high voltage bushing.
3. The neutral wire for the 3 phase set up above, is also the neutral for the single bushing transformer...that is why it is called single bushing...there is only one wire to it that is hot with respect to the case of the transformer. In reality, it should be called an auto-transformer, as that is how it is electrically configured.. And, every couple of poles, that neutral is fed down the pole, sometimes covered with a protective shield, to a long earth ground rod.
4. Out of the xfmr comes the two 120 volt hots, 240 total as they are opposite polarity..and the neutral connection, which is xfmr case, house center neutral, and return for the hv feed from the top of the pole. If the power company plays their cards correctly, there will be a net zero current on that neutral overall, but at each location, it will carry the current of the xfmr(s) that it is feeding.
5. The house wires will connect to the three wires. Typically, the neutral wire to the house will be the wire that supports the two hot wires...it will be anchored to the house, it will be bare, and the hots will twist around it.
6. For 3 phase building feeds, there will be 3 xfmrs, and 3 hots wrapped around the neutral.
7. For all residential installs in my area, the 3 wires go first to a meter pan, then down into the house breaker panel. By code, there will be a solid conductor, bare copper wire, that goes from the service panel, to the water pipe where it enters the building.
8. Within the house panel, all neutrals and grounds from the housefeeds are bonded together, to the ground wire, and to the neutral feed from the street.
My apologies to those who already knew this...
Now......the problem...
The neutral wire to the building was broken up where it connects to the pole wires...the hots were still connected, but there is no neutral connection.
So, how does a 120 volt appliance in the building work???
Simple..because the neutral to the pole is broken, all 120 volt appliances will have their return current go through the copper wire that is attached to the water pipe..
The problem? That wire is not sized for a real steady state load..it is sized only to clear a momentary fault..
And, it is in a location that is by design, begs for corrosion to break the continuity.
And the electrical continuity of the plumbing system may be compromised by either a dielectric isolation device (to prevent galvanic corrosion), or by one of those plastic whole house filters, an extreme electrocution hazard will be created..
Worst case scenario? The water pipe connection goes away...any single leg load will be able to raise the potential of the neutral and ground wires within the entire house to 120 volts.
Several appliances connected to the plumbing also have electrical ground connections...electric water heater comes to mind...So, it is possible that one of the appliances connects the entire building's plumbing to 120 volts..
Except of course, for the drains...
Imagine taking a shower, wet, standing in water, on a metal tub that is earthed via large copper drainpipe...and at some moment in time, a 1 KW space heater thermostat connects, finally popping the horribly corroded water pipe ground connection, making the pipe that feeds the shower head that is spraying you rise to 120 volts.
Nuff said.
If anyone ever, EVER sees this situation....do not hesitate to inform the people in the building that the situation warrants immediate attention by the electric company....this is, in fact, the second time I have seen this..
To all:
1. Check your external feed connection and make sure you have a good neutral feed...if not....immediately (and I really mean it) contact your electrical provider so that they can fix it..
2. Check your ground wire integrity...it is a failsafe device that is not just there to satisfy some arcane whim....as I point out, it can mean life or death worst case.
3. Make sure any device that breaks the plumbing ground integrity is doing what it is intended to do while not compromising the safety of the building.
For any questions of this nature, get the advice of a registered, licensed electrician in your area...do not ask me....do not ask anyone on a forum...do so with someone in your area who is qualified..
Cheers, John